Thanks Bill.
I agree that the Lamont is a lot easier to control. A similar boiler was built in England having no recirculation. It simply had the generator output entering low in the stand pipe. Baffles in the stand pipe forced a long path for steam to travel up through the water. The water in the stand pipe would be at saturation temperature. When you have a saturated mixture of steam and water entering the stand pipe the steam simply separated out to the top of the stand pipe. When you had superheated steam entering the stand pipe the super heat was given up to the water in the stand pipe as it traversed through the baffles to the top. The heat given up to the water caused evaporation making more saturated steam and lowering the water level. The stand pipe water level was simply controlled by the firing rate. Producing saturated steam mix raising the water level or superheated steam lowering the water level. Saturated steam was taken off from the top of the stand pipe. The comical boiler was for the dry cleaning industry and built to produce saturated steam. But for superheated steam it would be simple to run through a super heater section like a Lamont.
"It's been proven over many efforts that a dynamic feed system works best, with multiple feedbacks into the system."
What feed backs are there other then pressure and temperature in a mono-tube boiler?
The stand pipe adds water level to the control and provides a separation of water and saturated steam going to the super heater. You do not have control of the superheat temperature. Just assurance that you have superheat. The only control is fixed by the placement and length of the super heater, When industrial processes require very specific super heated steam temperature a separately controlled super heater is used.
I think I still did not explain the control system well enough. Let me try again
The control system has three inputs. Usage, Pressure, and Temperature.
Usage:
Actually it's not the feed that is dynamic, It' is the usage.
That is where the proportional feed pump comes in. It is in series with the load metering water into the steam generator in proportion to that being used by the engine. So when the throttle is suddenly opened the pump will respond feeding water at a higher rate. The feed proportional is for a specific pressure and temperature. The system does require the pressure to be held. Pressure is the feed back controlling the fire, heat input. This system does relay on pressure being held and may need some volume of steam reserve to dampen pressure fluctuations. The pump is also controlling the temperature. With a stable pressure the pump will pump less water when the temperature is low and more water when temperature is high.
As an argument of all the variables inside the boilers. The changing zones etc. All I can say is that experience has shown that the White flow-motor control system worked astonishing well. It didn't address all that internal goings on and worked quite well.
Some of the problems I am worried about is that specific volume ratio is not a single point but a line. I am trying to control for a specific pressure and temperature state output. But the specific volume that of that steam follow a line of changing pressure and temperature. The is lower pressure and temperatures having the same specific volume as well higher. So it is a line passing through my control point. Shown in the diagram below.
Looking at the constant specific volume ratio line above. Pressure horizontal and temperature vertical, If the steam state isto the left or above the constant ratio line excess water is being pumped. On the right or below the line too little water is being pumped.
A fully mechanical proportional system would have a piston fuel pump driven by the donkey pump. A mechanical linkage that can adjust the fuel pump stroke from the steam pressure.
The Lamont has a good quantity water at the saturation temperature in the stand pipe if it were to burst. That water would flash to steam just the same as a fire or water tube boiler. So there is some explosion hazard with a Lamont. it's not likely to suffer overheating failure as a water or fire tube boiler does in low water saturations. But in an accident the stand pipe could suffer collision damage and burst.